I need support from the forum on Perennial issues we have on one of our unit Fr-9E related to cooling water system.
Plant is 3x 9E DLN1 simple cycle,commissioned in 2003.
In the year 2006 on GT1B - we started seeing high temperatures on Aft leg reaching upto 100+ deg C (left side) & 85 deg C (right side) with ambient of 47+ deg C in summer when unit operated at base load.
Issue was communicated to GE and from then to till date they have verified entire system - orifice / pipings / blockage in cooling jackets of support legs / any leaks or bypass / VTR-1 & 2 functional checks / cooling water contamination / flow checks - water collection per minute.
Nothing Conclusive so for and they now asked to check flow across the orifice at various points which yet to be confirmed.
Another issue we are facing now is Flame scanners getting over heated and loosing counts while unit operated at primary modes and at peak hours with ambient of 47+ deg C all 4 primary flame scanners coubnts loosing leading to trip the unit on loss of flame while all other operational parameters normal.
GE suspect there steam forming inside the system due to high temperatures which is resulting into improper cooling of aft support legs / flame scanners. Hence we made temporary arrangements to vent the system to remove any air/ steam trap in the system by connecting tubing at the vent plug on the aft leg and this tubing we have connected back to expansion / make up tank to avoid any loss of cooling water. We are crack opening this vent line connected to legs whenever high temperature alarm appears to release any air / steam trap.
In spite of repeated followups & checks carried out GE failed to resolve this issue and now being summer we are facing big challenge to operate the unit.
What i want to understand?
1. What happened in the cooling system which resulted into aft support legs high temperatures - while after commissioning units run with no issues till 2006.
2. What is the source of cooling water getting hotter in this GT alone while GT1A /1B no such issues?
3. What can be done to resolve this issue? like increase orifice size? etc.
Any feedback from the forum is appreciated.
Thanks,
Arun.
Plant is 3x 9E DLN1 simple cycle,commissioned in 2003.
In the year 2006 on GT1B - we started seeing high temperatures on Aft leg reaching upto 100+ deg C (left side) & 85 deg C (right side) with ambient of 47+ deg C in summer when unit operated at base load.
Issue was communicated to GE and from then to till date they have verified entire system - orifice / pipings / blockage in cooling jackets of support legs / any leaks or bypass / VTR-1 & 2 functional checks / cooling water contamination / flow checks - water collection per minute.
Nothing Conclusive so for and they now asked to check flow across the orifice at various points which yet to be confirmed.
Another issue we are facing now is Flame scanners getting over heated and loosing counts while unit operated at primary modes and at peak hours with ambient of 47+ deg C all 4 primary flame scanners coubnts loosing leading to trip the unit on loss of flame while all other operational parameters normal.
GE suspect there steam forming inside the system due to high temperatures which is resulting into improper cooling of aft support legs / flame scanners. Hence we made temporary arrangements to vent the system to remove any air/ steam trap in the system by connecting tubing at the vent plug on the aft leg and this tubing we have connected back to expansion / make up tank to avoid any loss of cooling water. We are crack opening this vent line connected to legs whenever high temperature alarm appears to release any air / steam trap.
In spite of repeated followups & checks carried out GE failed to resolve this issue and now being summer we are facing big challenge to operate the unit.
What i want to understand?
1. What happened in the cooling system which resulted into aft support legs high temperatures - while after commissioning units run with no issues till 2006.
2. What is the source of cooling water getting hotter in this GT alone while GT1A /1B no such issues?
3. What can be done to resolve this issue? like increase orifice size? etc.
Any feedback from the forum is appreciated.
Thanks,
Arun.