Q
Dear All members of Control.com
I am working on power plant 1200MW, we apply Wika T32 temperature transmitter for BFP winding & bearing temperature (8pcs) but by the trend on DCS we found that sometime temperature drop to -4.2degC and quickly recovers. It happened randomly and repeatedly.
It will trip BFP if the temp > 140degC, -4.2degC is alarm direction of transmitter we set to Lo if we set Hi, the pump will trip frequently. T32 was configured to RTD 3Wire measurement.
First, we doubt to RTD element, but when we change T32 to Rosemount and keep the monitoring for more than 1 week, signal drop is not coming anymore (not intend to blame Wika and glad to rosemount)
I have two question.
1. What condition make the T32 alarm active? (such as loss of the element RTD wiring ....?) Please let me know all conditions that T32 alarm activate.
2. Is the transmitter fail or any setting to solve problem?
Any advice would be highly appreciate.
I am working on power plant 1200MW, we apply Wika T32 temperature transmitter for BFP winding & bearing temperature (8pcs) but by the trend on DCS we found that sometime temperature drop to -4.2degC and quickly recovers. It happened randomly and repeatedly.
It will trip BFP if the temp > 140degC, -4.2degC is alarm direction of transmitter we set to Lo if we set Hi, the pump will trip frequently. T32 was configured to RTD 3Wire measurement.
First, we doubt to RTD element, but when we change T32 to Rosemount and keep the monitoring for more than 1 week, signal drop is not coming anymore (not intend to blame Wika and glad to rosemount)
I have two question.
1. What condition make the T32 alarm active? (such as loss of the element RTD wiring ....?) Please let me know all conditions that T32 alarm activate.
2. Is the transmitter fail or any setting to solve problem?
Any advice would be highly appreciate.