We are having GE frame 6E gas turbine with Mark V control system.
we had been running our machine on Natural gas for last 8 years but because of change in scenario we have again moved to light naphtha as fuel.
since then we are facing high spread issues.
After taking sd we replaced the fuel nozzles with the reconditioned nozzles and again run the m/c, spread went upto 70 deg on 12 MW only.
Then we replaced the nozzles with brand new fuel nozzles, replaced both liquid fuel and purge air check valves, replaced flow divider with new calibrated one. again after starting, spread values were around 30 deg when the load was 25 MW, then after increasing the load to 30 MW, spread increased to 90 deg.
We may again have to stop m/c because of such high value.
but what may be the other reason for this which we can check and replace. Is there be any damages in the combustion chamber which may cause this or the exhaust thermocouples may be faulty?
we had been running our machine on Natural gas for last 8 years but because of change in scenario we have again moved to light naphtha as fuel.
since then we are facing high spread issues.
After taking sd we replaced the fuel nozzles with the reconditioned nozzles and again run the m/c, spread went upto 70 deg on 12 MW only.
Then we replaced the nozzles with brand new fuel nozzles, replaced both liquid fuel and purge air check valves, replaced flow divider with new calibrated one. again after starting, spread values were around 30 deg when the load was 25 MW, then after increasing the load to 30 MW, spread increased to 90 deg.
We may again have to stop m/c because of such high value.
but what may be the other reason for this which we can check and replace. Is there be any damages in the combustion chamber which may cause this or the exhaust thermocouples may be faulty?