We are having generator synchronizing issues with 3 generators in parallel using a cross current (reactive differential) loop circuit. We have gen A, gen B, and, gen C in that order. We are using AB CGCM for the load share controls.
The problem we are having is that generator B will not synch nicely with other generators A or C. Generator B will try to take all the load and the kVARS are exceeding high compared to the other units. There is no issue with synching generators A and C together though.
Also noticed the voltage setpoint for generator B is 4153 with generator voltage at 4158 (4160 system). Voltage set point for generator C is 4200 with voltage around 4160, and the bus voltage is 4157.
Could this be a cross current CT wired backwards with generator B?