3phase 3 wire 240 volt. ..A phase to ground 240volt...Bphase to ground 0 volts ..C phase to ground 240volt. .leg to leg 240volt where is B phase grounded at?
Typically a Grounded B-Phase System has either the X2 terminal grounded at the transformer secondary or X2 connection is run to the system [first] disconnecting means and treated as a grounded conductor there (i.e. not fused or switched), though there is a variation using a 3-pole, common-trip circuit breaker because it opens all poles on trip including the grounded conductor.
It sounded funky to me at first as well, but it's just 3 240-volt phases with one corner grounded. Sounds like 127/240 3-phase Wye systems I've run into in the past, except it's a Delta not a Wye.
And it is impossible to undo a thumbs-up or thumbs-down. Once there is a thumb, there is no way to have no-thumb
>> These numbers don't work for the phase. It almost seems like 480 volts
>> single phase with the center tap grounded.
> Sounds OK to me. Sounds like a delta with one corner grounded.