I have some questions regarding the Start Checks. I need your experience with Mark VIe can help me? What does each permissive? Why each is activated?<pre>
START CHECK 0:
1.- IGV Position feedback trouble?
2.- Customer permissive to start?
3.- State of E-Stop1?
4.- Trolley crane not in storage?
5.- Sensor faults - inhibit start?
6.- Fire protection system trouble?
7.- Control system fault - start inhibit?
8.- SSOV startup permissive?
9.- IBH Manual valve closed?
10.- Servo no suicide start check?
START CHECK 1:
1.- Lube oil tank temp-normal?
2.- Generator no breaker not closed?
3.- flame detector trouble?
4.- Control mode off?
5.- Hydraulic accumulator N2 charge pressure?
6.- Breaker ground switches open?
START CHECK 2:
1.- Loss of master protective?
2.- Master protective startup trip?
3.- Comp bleed vlv fault pos lockout?
4.- Static starter ready to start?
5.- Hydrogen start check?
START CHECK 3:
1.- Vibration start inhibit?
2.- Exciter ready to start?
3.- Master protective trip?
4.- Minimum speed signal?
5.- EGD Link to the exciter is bad?
6.- EGD Link to the LS2100 fault?
START CHECK 4:
1.- Atom air comp start check?
2.- Atomizing air purge sys start check?
3.- Water inj purge sys start check?
4.- Liq fuel pump sys start check?
5.- Gas purge start check?
6.- FSD position lockout trouble?
7.- N2 purge active/purged - LF startup lockout?
8.- Hazardous gas system start check?
9.- Hydraulic protective trouble lockout?
AUX READY TO START:
1.- Start check?
2.- Gen breaker close/open status input?
3.- Auxiliary check - servos?
4.- AII IO Packs communicating?
5.- Multiple start permissives?
6.- Pre-start tests passed - ready to start?
7.- Cooldown slow roll start speed relay?</pre>
Thanks a lot for the help .
START CHECK 0:
START CHECK 1:
START CHECK 2:
START CHECK 3:
START CHECK 4:
AUX READY TO START:
1.- Start check?