E
After half an hour to synchronize the unit, the temperature matching once activated. the unit switches the mode of combustion of 1D to 3D. in 3D in a minute the GT trip, to be lost hit LOB blocking in the valves of purge VA13-3 and VA13 -4 of the G3 gas line, by high pressure between the valves and pressure switches activated causing the signal of trip of the unit. Tras perform checks on sealing and time open/close valves of purge, vent valve VA13-12 and calibration pressure switches, two hours after it restarts the unit and the combustion mode switching, is without problems remain for 30 minutes in 3D, start the unit without problem.
The next day a restart is performed, trip again, and restart the unit. In the second start VA13-12 purge valve is changed.
In the first start, after a 12 hour to stop the unit,in 3D mode combustion (in previous starts of the unit remains for 1 minute and changed to 6.2 without problems) in these last starts trip.
Because at the first start the change is done in 1 minute and the second remains 30 minutes in 3D, when the second star the has made the warming of the HRSG, it has been the HRSG heated for 30 minutes.
Which may be the cause of the trip?
Thank you