J
Dear All
After CI, Frame 6 GT Mark V simple Cycle, flame out occurred and tripped the unit at FSNL. Activities carried out during CI
1.Duel fuel nozzle replaced
2.Liner & TP replaced
3.Cross fire tube replaced
4. SRV & GCV serviced
Observations:-
first flame out happened Can # 7 at 81% TNH
Second flame out happened Can # 3 at 99% TNH
Third flame out happened Can # 2 at FSNL
FPG2 pressure was OK all the time (at FSNL 16.5 Bar)
GCV opening was OK
IGV opening was OK
Gas flow disturbance not found.
Kindly advice what to do?