D
Good afternoon all.
I have just got off the phone with an engineer who is telling me that the neutral of a generator is being switched to open when in parallel with the mains.
We have mains incomer @ LV 4 pole ACB
Generator incomer @ LV 4 pole ACB
Load connected in between.
The set can operate in island and in parallel.
In island the neutral (not neutral earth connection) contactor remains closed. However when run in parallel the contactor opens.
It is not a neutral earth connection that is being switched but the neutral itself.
Therefore when in parallel with the mains this generator is connected to it with its neutral disconnected.
Also the generator neutral is bonded to earth directly in the alternator.
Does this seem normal to you guys?
Normally in my mind we have only one star point connected to ground when in parallel. Usually the mains neutral earth connection remains and we open the generator neutral earth connection.
Any questions or ideas?
Thanks for your time.
I have just got off the phone with an engineer who is telling me that the neutral of a generator is being switched to open when in parallel with the mains.
We have mains incomer @ LV 4 pole ACB
Generator incomer @ LV 4 pole ACB
Load connected in between.
The set can operate in island and in parallel.
In island the neutral (not neutral earth connection) contactor remains closed. However when run in parallel the contactor opens.
It is not a neutral earth connection that is being switched but the neutral itself.
Therefore when in parallel with the mains this generator is connected to it with its neutral disconnected.
Also the generator neutral is bonded to earth directly in the alternator.
Does this seem normal to you guys?
Normally in my mind we have only one star point connected to ground when in parallel. Usually the mains neutral earth connection remains and we open the generator neutral earth connection.
Any questions or ideas?
Thanks for your time.