PLC ABB Pluto -- HMI ABB CP651

M

Thread Starter

Mike76

Hello guys,

I have 3 PLCs ABB Pluto B46 connected on a RS485 network (2 wires). Each one is located in a different station and connected with an HMI ABB CP651.

My programs on the PLCs are working properly but I haven't found the way to import the tags from each PLC to each HMI. I'm using the softwares PLUTO MANAGER (PLC) and PANEL BUILDER 600 (HMI). It seems to be a communication problem because I haven't selected the proper protocol. I tried to use ABB Modbus RTU protocol but in the PANEL BUILDER 600 I have to import the tags on a .exp file and it's impossible for me to generate this file from the PLUTO MANAGER, so if any of you was through this and could give me a hand I would appreciate it.

Kind Regards...
 
Thanks a lot. It worked with Modbus RTU in ASCII mode and the port communication speed: 57600 Mbps.

In the last version of Panel Builder 600 (v2.0) there's a specific protocol for Pluto PLCs (ABB Pluto).
 