Hello there?
Recently we are facing Combustion trouble- alarm in one of our GTs (frame 6B) with DLN system. It has Mark6e control system. During de-loading of that machine, while it reaches around 21 MW from Base load it generates Combustion Trouble-alarm just before of DLN transfer. Surprisingly CT-alarm does not appear all the time of de-loading. For example if we de-load 10 times from Base to 20 MW load it generates CT-alarm for 6 or 7 times.
From Mark6e trend it was observed that GCV starts hunting with GT load hunting (21 MW to 23 MW) and CAN 2 & 8 (FD-6 and FD-7) becomes flame out (lower threshold limit 16%) while P2 pressure and GSV remain steady.
Several times GCV and GSV servo replaced and calibration done accordingly to troubleshoot the combustion problem. It should be noted that servo current and LVDT FB found very normal during calibration each time and also during runtime of GT all gas valves reference command and Feedback remain almost same (very insignificant error observed). For your better understanding I would like to share two trends (one with CT-alarm another without CT alarm) in excel csv format of the same GT. Please follow the link below:
https://www.dropbox.com/s/xap0mwegrzm0m38/With CT Alarm.csv?dl=0
https://www.dropbox.com/s/7f2t0gtep26shbg/Without CT Alarm.csv?dl=0
Please don't be confused about P2 pressure in the trend. For some other reason SRV is adjusted to maintain P2 pressure around 19 bar earlier it was set to 15 bar.
Recently we are facing Combustion trouble- alarm in one of our GTs (frame 6B) with DLN system. It has Mark6e control system. During de-loading of that machine, while it reaches around 21 MW from Base load it generates Combustion Trouble-alarm just before of DLN transfer. Surprisingly CT-alarm does not appear all the time of de-loading. For example if we de-load 10 times from Base to 20 MW load it generates CT-alarm for 6 or 7 times.
From Mark6e trend it was observed that GCV starts hunting with GT load hunting (21 MW to 23 MW) and CAN 2 & 8 (FD-6 and FD-7) becomes flame out (lower threshold limit 16%) while P2 pressure and GSV remain steady.
Several times GCV and GSV servo replaced and calibration done accordingly to troubleshoot the combustion problem. It should be noted that servo current and LVDT FB found very normal during calibration each time and also during runtime of GT all gas valves reference command and Feedback remain almost same (very insignificant error observed). For your better understanding I would like to share two trends (one with CT-alarm another without CT alarm) in excel csv format of the same GT. Please follow the link below:
https://www.dropbox.com/s/xap0mwegrzm0m38/With CT Alarm.csv?dl=0
https://www.dropbox.com/s/7f2t0gtep26shbg/Without CT Alarm.csv?dl=0
Please don't be confused about P2 pressure in the trend. For some other reason SRV is adjusted to maintain P2 pressure around 19 bar earlier it was set to 15 bar.