We usually calculate compressor efficiency by this method for the past 10 years and based on that we planned for a compressor off-line wash.
ηIsen =
T1 = Actual compressor inlet temperature (ºR)
T2 = Actual compressor outlet temperature (ºR)
P1 = Compressor inlet pressure (Psia)
P2 = Compressor outlet pressure (Psia)
k = Ratio of specific heats = 1.4
<b>Moderator's note:</b> I think ηIsen and (ºR) are special characters that did not show up correctly.
Based on that formula our compressor efficiency was calculated.
Values were P2=203 Psi, P1=14.14 Psi, T1=79.8 F, T2=799 F and efficiency showed 86% Approx.We do have Evap system ON (Method of turbine inlet cooling) during this period.
Now the scenario has changed and we stopped evap system and installed a new system which is called Wet Compression system (Method of turbine inlet cooling). This system reduced 4~5 degrees more temperature drop of compressor inlet temperature (T1) than evap system and also about 50degree temperature drop in Compressor discharge temperature (T2).
When we calculate the compressor efficiency it crossed 95%. We were like wohhhh what we will do now? How will we establish our offline wash and another question came into mind that whether this efficiency formula is correct? Because in winter season fully cleaned compressor shows efficiency to reach about 87%, while in summer fully cleaned compressor efficiency shows 86%?. Please guide.
(Our turbine is Siemens Westinghouse W251 B11, 48.8MW ISO,Operating in combined cycle mode)
ηIsen =
T1 = Actual compressor inlet temperature (ºR)
T2 = Actual compressor outlet temperature (ºR)
P1 = Compressor inlet pressure (Psia)
P2 = Compressor outlet pressure (Psia)
k = Ratio of specific heats = 1.4
<b>Moderator's note:</b> I think ηIsen and (ºR) are special characters that did not show up correctly.
Based on that formula our compressor efficiency was calculated.
Values were P2=203 Psi, P1=14.14 Psi, T1=79.8 F, T2=799 F and efficiency showed 86% Approx.We do have Evap system ON (Method of turbine inlet cooling) during this period.
Now the scenario has changed and we stopped evap system and installed a new system which is called Wet Compression system (Method of turbine inlet cooling). This system reduced 4~5 degrees more temperature drop of compressor inlet temperature (T1) than evap system and also about 50degree temperature drop in Compressor discharge temperature (T2).
When we calculate the compressor efficiency it crossed 95%. We were like wohhhh what we will do now? How will we establish our offline wash and another question came into mind that whether this efficiency formula is correct? Because in winter season fully cleaned compressor shows efficiency to reach about 87%, while in summer fully cleaned compressor efficiency shows 86%?. Please guide.
(Our turbine is Siemens Westinghouse W251 B11, 48.8MW ISO,Operating in combined cycle mode)