Now days Boiler water level calculation is compensated by making use of the boiler drum pressure corresponding water density and steam density according to the Boiler pressure.
Example the boiler drum tap to tap distance was 770 MM, operating pressure was 42 bar, the calibration range traditional method was 0 to 595 mm with elevated zero.
The question is transmitter calibration. while drum pressure corresponding steam density algorithm in place the transmitter calibration is actual Tap to tap distance say 0 to 770 mm or calibration is 0 to 595 MM?
(the actual calibration can be treat as -770 mm to 0 or -595 mm to 0)
Regards
Rakesh
Now days Boiler water level calculation is compensated by making use of the boiler drum pressure corresponding water density and steam density according to the Boiler pressure.
Example the boiler drum tap to tap distance was 770 MM, operating pressure was 42 bar, the calibration range traditional method was 0 to 595 mm with elevated zero.
The question is transmitter calibration. while drum pressure corresponding steam density algorithm in place the transmitter calibration is actual Tap to tap distance say 0 to 770 mm or calibration is 0 to 595 MM?
(the actual calibration can be treat as -770 mm to 0 or -595 mm to 0)
Regards
Rakesh