Siemens SGT300 Flame Failure

A

Thread Starter

anvay

Hello Every one,

This is my first post so please ignore if some mistakes will be there.

Actually we are facing the problem for completing the sequence for Siemens SGT-300, at around 13200 rpm machine is tripped and message is "CAN FLAME FAILURE DETECTED" when we are running on diesel (for gas it is not even ignite) and showing errors on 2 exhaust thermocouples out of 13. we checked all the possibilities like exhaust thermocouples swapping, combustion chambers thermocouples, clean burners. all reading like VGV, PT8, temp. variations, fuel intake, are nearly same with the last healthy startup.

Please give some valuable suggestions.
Thanks
 
You've been thermocouple swapping?!

The symptoms suggest burner failure although you haven't indicated loading at trip point. If you have cleaned the offending burner, try a direct replacement.

It is generally easier to start on gas rather than liquid fuel. Why will it not start on gas?
 
Thanks for the reply, can you plz elaborate what do you mean by direct replacement?

And also we tried on gas but in that case even it is not ignited.

> You've been thermocouple swapping?!
>
> The symptoms suggest burner failure although you haven't
> indicated loading at trip point. If you have cleaned the
> offending burner, try a direct replacement.
>
> It is generally easier to start on gas rather than liquid
> fuel. Why will it not start on gas?
 
M

Martin Andrade

Hi

We can support your issues with the SGT300 controls system. We are a specialist turbine service provider focusing purely on the Siemens SGT range of gas turbines, including the SGT100, 200 and 300.

Supporting the engines both on the mechanical side and control systems. We support engines around the world including Europe, US, Africa and Asia. If you still require assistance with this issue please do not hesitate to contact us, my number is +44 (0) 7710 307554.

Regards
Martin
 
D
Hi, i have the same failure in SGT-400, i replaced de burner number 2, because de failure was in TCs 2 and 3. but the failure is again in the machine.

I need Help !!!

>Actually we are facing the problem for completing the
>sequence for Siemens SGT-300, at around 13200 rpm machine is
>tripped and message is "CAN FLAME FAILURE DETECTED" when we
>are running on diesel (for gas it is not even ignite) and
>showing errors on 2 exhaust thermocouples out of 13. we
>checked all the possibilities like exhaust thermocouples
>swapping, combustion chambers thermocouples, clean burners.
>all reading like VGV, PT8, temp. variations, fuel intake,
>are nearly same with the last healthy startup.
 
Hi

We can support your issues with the SGT300 controls system. We are a specialist turbine service provider focusing purely on the Siemens SGT range of gas turbines, including the SGT100, 200 and 300.

Supporting the engines both on the mechanical side and control systems. We support engines around the world including Europe, US, Africa and Asia. If you still require assistance with this issue please do not hesitate to contact us, my number is +44 (0) 7710 307554.

Regards
Martin
Hello Mr. Martin,

This is Yasin GUL from Teccof Group in Turkiye.

We have some problems about SGT-300 Gas Turbine spare parts, could you supply spare parts? Please check attached!

If yes, please call me my number +90 545 475 17 17 or send email [email protected]

Regards
Yasin
 

Attachments

Top