We have four gas turbines at or site, three of them are operated via Mark-V and one of them is operated via Mark-VI.
All gas turbines are frame-5 machines of with capacities of 24.6MW (Mark-VI), 13.8MW, 13.8MW and 11.2MW.
The turbine operating on Mark-VI indicated a difference in its MW reading in two megawatt transducers. Both transducers were reading 14.9MW on their local display but in Mark-VI dwatt_1 was reading as 17.2MW and dwatt_2 was reading as 14.9MW. Now due to high selector logic of Mark-VI, dwatt was reading as 17.9 MW. The range of both megwatt transducers is -1 to 35 MW.
This difference was gradually increasing. So it was decided to check the mA signals coming from the transducers to Mark-VI termination boards. To check the current in these transducers loop, we had to disconnect the loop and check the loop current. For this activity the value of dwatt_1 was forced to 17.2 MW. After the checks, the signal dwatt_1 was unforced but suddenly the value of dwatt_1 jumped to 41.72MW, causing the gas turbine to suddenly shed its load to as low as 0.5MW. The logic was forced back in order to avoid the tripping.
So after experiencing the above explained scenario, there are a few questions that need to be answered:
1. As mentioned above, there is a HIGH SELECTOR to select the high MW value. Logically speaking, if one of the transducers failed, its value should go down rather than going higher so that it is ruled out from the calculations. Is there any logic in Mark-VI which identifies failed MW transducers & rule them out from the calculations. Furthermore, if the transducer failed, why did the value jumped up to 41.72MW, 20% above the maximum limit. Is it a fail safe?
2. When the transducer value was read as 41.72 by Mark-VI, why did gas turbine shed the load so rapidly? (Trends show the load was shed in about 9 seconds). Since the gas turbines are running in droop mode, why the FSR was not controlled by the speed control block?
3. Since it is now known that one of the transducers has failed and considering that the turbine is running at a load of 17.2MW, at what value should the unhealthy transducer be forced to avoid any undesirable consequences?
Kindly also comment the role of dwatt signal in FSR calculation during normal operation of the gas turbine.
Any help would be appreciated!
All gas turbines are frame-5 machines of with capacities of 24.6MW (Mark-VI), 13.8MW, 13.8MW and 11.2MW.
The turbine operating on Mark-VI indicated a difference in its MW reading in two megawatt transducers. Both transducers were reading 14.9MW on their local display but in Mark-VI dwatt_1 was reading as 17.2MW and dwatt_2 was reading as 14.9MW. Now due to high selector logic of Mark-VI, dwatt was reading as 17.9 MW. The range of both megwatt transducers is -1 to 35 MW.
This difference was gradually increasing. So it was decided to check the mA signals coming from the transducers to Mark-VI termination boards. To check the current in these transducers loop, we had to disconnect the loop and check the loop current. For this activity the value of dwatt_1 was forced to 17.2 MW. After the checks, the signal dwatt_1 was unforced but suddenly the value of dwatt_1 jumped to 41.72MW, causing the gas turbine to suddenly shed its load to as low as 0.5MW. The logic was forced back in order to avoid the tripping.
So after experiencing the above explained scenario, there are a few questions that need to be answered:
1. As mentioned above, there is a HIGH SELECTOR to select the high MW value. Logically speaking, if one of the transducers failed, its value should go down rather than going higher so that it is ruled out from the calculations. Is there any logic in Mark-VI which identifies failed MW transducers & rule them out from the calculations. Furthermore, if the transducer failed, why did the value jumped up to 41.72MW, 20% above the maximum limit. Is it a fail safe?
2. When the transducer value was read as 41.72 by Mark-VI, why did gas turbine shed the load so rapidly? (Trends show the load was shed in about 9 seconds). Since the gas turbines are running in droop mode, why the FSR was not controlled by the speed control block?
3. Since it is now known that one of the transducers has failed and considering that the turbine is running at a load of 17.2MW, at what value should the unhealthy transducer be forced to avoid any undesirable consequences?
Kindly also comment the role of dwatt signal in FSR calculation during normal operation of the gas turbine.
Any help would be appreciated!