K
In case of total power failure in the grid, the running gas turbine trips. We have naphtha as running fuel in our facility & we will do a heavy fuel purge. The machine will come on DC barring gear or if that fails, we will do hand barring. Now, a black start diesel generator with pressurized starting air is available at our facility for, which we will use to charge the GTP MCC switchgear, which houses the various LT AC auxiliaries for the gas turbine like AOP, AC JOP, etc & put the machine on AC barring gear. Again, using the diesel generator set, we start the cranking motor of the gas turbine & take it up to FSNL. Next, the field breaker of the excitation circuit of the brushless generator is closed & generator terminal voltage is brought to less than 1 kV [Usual value is 10.5 kV]. The same is done to prevent any inrush current in the generator transformer [supplying to grid at 220 kV]. Next, the isolators of the generator transformer are closed & the generator circuit breaker is closed in dead bus mode. Then, the excitation voltage is raised so as to bring the generator terminal voltage to 10.5 kV, the normal value. Now, the unit auxiliary transformer [which is connected to the LV side (10.5 kV) of the generator transformer], needs to be synchronized to the 6.6 kV bus (which has the gas turbine starting motor & currently being energized by the diesel generator)]. Now, my doubt is what pre-select load set point to be given to the gas turbine? Is a low value like 0.3 MW possible? Or should we go for isochronous mode of operation (islanding mode)? I have seen this option in the Mark 5 HMI operating screens, but I have never used it? We have 2 gas turbines, both frame 9E & 115 MW base load each and Mark 5 control system. Has anyone operated their gas turbine in this islanding mode?