This site has Mark V turbine controls for eight of its 7FAs. While performing the verify current to determine the validity of the LVDTs, the Mark V applies a small amount of negative current required to ramp the gas valve open, then reverses the current to ramp the gas valve closed. This occurs on all gas valves and IGVs on 7 of our 8 units. But for one unit, the SRV does not open. It appears to perform the test but when you view verify the valve feedback is either a flat line or a very low peak with a kink at 30% and 70%. The auto calibration works as expected and the null bias looks great at the factory setting of 2.67. The current gain match settings of the other units. I've replaced the RVDT and the servo and various null bias settings with the same results. I suspect that a Mark V card is bad that provides the reference for the op amp to drive the servo current. If this is correct, which board would perform this function? This is an HMI configuration, and the regulator changes from 77 to 43 as it should during the test to ignore the P2 pressure feedback.
Thank you in advance for your time,
Jack