Siemens to GE Fanuc PLC Communication with Modbus RTU
dheerendar
I need to connect by Siemens S7-300 PLC (CPU315-2 DP) to fetch data from GE Fanuc VersaMax Micro PLC (IC200UDD110) through Modbus RTU. But i have no idea how to do it.
Please help.
Thank You
[email protected]
Hello Dheerendar,
A starting point is to decide if the GE Fanuc VersaMax Micro PLC is acting as Modbus RTU master or Slave. There are Siemens solutions for Modbus RTU, but I would suggest using a gateway as it is more cost effective.
As the S7-300 is normally a Profibus master, you will need:
https://www.anybus.com/products/gat...nicator/detail/anybus-communicator---profibus
If the GE Fanuc VersaMax Micro PLC is acting as Modbus RTU Slave.
And you will need:
https://www.anybus.com/products/gat...bus-x-gateway-profibus-slave-modbus-rtu-slave
If the GE Fanuc VersaMax Micro PLC is acting as Modbus RTU master.
My 2 cents
Patrick L