Wednesday, April 25, 2018
Generator Rotor Earthing
Generator rotor earthing on a frame 6B generator
We are inspecting the rotor earthing on a frame 6B generator at the exciter end and request if someone could please explain how it is supposed to work and the theory behind it. We have a measurement brush, a check brush, a brush control power supply, a rotor earth test pushbutton, a timer set for a 10 second on pulse every 10 hours. Interpreting the drawing suggests that when the machine is running (field on) the measurement brush is engaged for 10 seconds then every 10 hours for another 10 seconds, or when the test pushbutton is pressed and when the machine is off the test pushbutton engages the test brush. We assume the test brush should bring up a rotor earth fault and the measurement brush should not - so it's testing the rotor earth protection which is why the test brush can only be engaged when the machine is off to prevent a trip.
Have I got this right? thanks.
David
Hi
The relay circuit protection test is carried out when it is stopped by a test device that measures resistance between revolving and ground files.
Siemens' sensor system conducts the test, and the generator is switched off by pressing a protection button that gives the test value.