Thursday, May 24, 2018
1734-IE8C Major Channel Fault
1734-IE8C input module went bad. Replaced module still all channels solid red.
Need help troubleshooting 1734-IE8C input module. All channels show solid red so I replaced the module and had the same results. Any and all help would be appreciated.
Moderator's Note: 1734-IE8C is manufactured by Allen-Bradley
By Bob Peterson on 16 June, 2017 - 3:31 pm
Blinking red on the channel indicator usually means out of range. no idea what solid red means and the AB literature is not especially helpful other than suggesting it is a more serious error.
Knowledge base article 493193 suggests:
A solid red LED condition on these modules is caused by having no field power applied to the POINT I/O bus.
When using a 1769-L16 or 1768-L18 controller with these POINT I/O modules, make sure that FP+ and FP- pins on the controller have 24VDC applied to them.
If using the modules with a 1734-PDN adapter verify the V and C terminals of the adapter are receiving 24VDC as well.
Bob
http://ilbob.blogspot.com/
Check the field power supply to the PLC FP+/FP- pins (if they're part of a CompactLogix chassis) or PDN adapter V/C pins:
https://rockwellautomation.custhelp.com/app/answers/detail/a_id/493193
(access level: everyone, you need a free login)
Installation manual:
http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1734-in033_-en-e.pdf