Wednesday, April 25, 2018
Data Configurations
APM directory configurations
Hello members, can somebody explain these terms, used while configuring data point.
Calculated PV
RAW VALUE
PV HIGH RANGE IN ENGINEERING UNIT
PV LOW RANGE IN ENGINEERING UNIT
PV EXTENDED ENGINEERING UNIT RANGE HIGH
PV EXTENDED ENGINEERING UNIT RANGE LOW
From the APM noted in title and the parameters asked this I assume you are asking about a Honeywell advanced process manager. Check these links out. Or search for APM manuals via Google. Feels like Honeywell has more available these days than they use to.
APM control theory theory manual
https://www.honeywellprocess.com/library/marketing/product-manuals/AP09-600.pdf
Hpm parameter dictionary
https://www.honeywellprocess.com/library/marketing/product-manuals/HP09-540.pdf
Some of this varies on point specifics but normally:
PVRaw is pct of the input.
Pvcalc is the value of the input converted from raw input to engineering units
PVHI is the value in engineering units at 100%
PVLo is the value in engineering units at 0%
Extended range hi lo are the values that the beyond 0% and 100%. Above/below the extended range the PV will be clamped or set to NAN- not a number
Thank You Sir for your answer. Are you working or ever worked on TDC 3000 Honeywell?