We have a Modicon TSX Premium PLC and currently has a "Low Battary Fault Blinking" and PLC cannot run
Hi ALL,
We have a Modicon TSX Premium PLC-Processor TSX PSY1610. The "Low Battery Alarm" was active on local HMI for some months until the PLC stopped working yesterday. What is the software used to program the modicon premium PLC and how can I talk to the processor?
Thank you
Chris
Chris,
You will need Schneider Unity Pro Medium, Large or Extra Large programming software (dependent on your CPU model. The TSXPSY1610 you mentioned is a power supply) and to talk to the processor via the software you will need a n 8-way female mini-DIN connector programming cable. Next you will need to replace the battery
Rich
Thanks Rich,
Appreciate your help
Chris
1 out of 1 members thought this post
was helpful...
The PLC should remain running with the alarm on but you may have had a power failure in which case the configuration is probably gone.
You will need to locate a copy.
The battery is normally changed without removing the power, at least that's the way it was when I last used Modicon.
If you don't want to go to the expense of purchasing the software I'm sure you can find a consultant to reload it for you.
1 out of 1 members thought this post
was helpful...
Roy is correct. I made the assumption that the reason that your PLC stopped working was due to a power interruption in which since the battery was dead then your program would be bits distributed throughout cyberspace or somewhere like that. Hopefully you have an archived copy somewhere to go off of. Like Roy said, contact a integrator or find a Schneider ACE distributor.
You have clicked on the "?" button for search help. To search the
site, enter your search terms in the box labeled "search the site"
and hit Enter.
Some tips for better search results...
- Precede each search term with a "+", as follows:Otherwise, any post with either term will match.
- Use double quotes around phrases, as follows:
- +"Allen Bradley" +ethernet
Otherwise, posts containing these words in separate locations will match. - To exclude a word, precede it with a "-", as follows:This will return only posts containing "Modbus" but NOT containing
"Plus".
- Note that common words (and, that, etc.) and words shorter than 2 characters
are automatically excluded from searches.
You must be a Control.com member
to subscribe to threads. Please log in and try again.
If you're not already a member, consider joining. It's free,
and you can customize the content you view, as well as being
able to subscribe to threads and topics, getting new posts
delivered to your email as they appear.
You must be a Control.com member
to vote on a post. Please log in and try again.
If you're not already a member, consider joining. It's free,
and you can customize the content you view, as well as being
able to subscribe to threads and topics, getting new posts
delivered to your email as they appear.