Monitoring a flow sensor over a 4-20mA signal
Need help with verifying 420mA wiring and devices
We have a customer that has a DCS that is monitoring a flow sensor over a 4-20mA signal. We do not have any info on their DCS.
They would like to add a local display(for the flow) out near the sensor. And the displays that would be used is a Omron# K3HB-XAD 24VAC/VDC with a option card inside of it that can transmit a 4-20mA as well (Omron# K33-L1A)
https://www.ia.omron.com/products/family/1535/specification.html
The flow sensor is a FLOTECH F6206-AIV-DS
https://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=3&cad=rja&uact=8&ved=0ahUKEwiKlcHf4NTWAhVNGsAKHWjEAFYQFgg0MAI&url=https%3A%2F%2Fwww.instrumart.com%2Fassets%2FFlo-tech-Activa-Ultima-Classic-Quad-Sensor-Manual.pdf&usg=AOvVaw0n8qYNOYO8_A9v6tZDN6ae
My question is: Can i just add the Omron display in series between the flow sensor and the DCS, using the current + and - on the display?
or do i need to use the retransmit capabilities?
You might want to take a look at the "Precision Digital" Model PD6720-0K1.
It is loop powered and doesn't require extra power wires or retransmit requirements. It also provides a NEMA 4X / IP65 enclosure. It also can display flow rate as well as totalizer with reset.
https://www.predig.com/pd6720
https://www.predig.com/indicatorpage/back-basics-fundamentals-loop-powered-devices
>My question is: Can i just add the Omron display in series between the flow sensor and the DCS, using the current + and - on the display? or do i need to use the retransmit capabilities?<
The short answer is Yes
But I agree with Feuchtde, get a modern 2 wire 4-20mA display
No you don't need to use the re-transmit option in fact avoid it.
I didn't try and verify the transmitter will handle the additional load (extra resistance) but it would be unusual to find a modern transmitter that can't handle at least 600 Ohms,
Roy
By Fabricio Andrade on 28 November, 2017 - 8:34 am
In short, yes you can do it without any problem.
Additionally, if your device is also HART, you can use a device such as the tri-loop to split the HART input in up to 3 analog output, and then the installation will look better.