I'm having a problem of underdand the reason of the output of a system.
Hi guys,
Can anyone here explain me what are the reasons that the output of the following system is always zero?
A = [-0.2,0.0,0.0;0.0,-0.3,0.0;0.0,0.0,-0.7];
B = [0.0;0.0;2.5];
C = [0.0,2.6,0.0];
D = [0.0];
I tried to simulate in matlab:
[Y,X]=dstep(A,B,C,D,1,100);
stairs(Y);
Thanks in advance!
1 out of 1 members thought this post was helpful...
Hello Thiago,
Your D-matrix is zero, so there is no direct throughput from input to output, i.e. any non-zero output has to come from the states of the system.
>B = [0.0;0.0;2.5];
>C = [0.0,2.6,0.0];
>D = [0.0];
<snip>
Your input-matrix B only has a non-zero element on Row 3, i.e. the input only directly affects the third state. The state matrix A is diagonal, so that the three states do not affect each other.
Your output matrix C only has a non-zero element in the second column, i.e. the output is only affected by the second state. However, since A is diagonal and B is only non-zero in its third row, the second state is not affected by the third state or the input, i.e. it always stays zero. Thus, the output also always stays zero.