Allen Bradley Tag Export
Export file does not have ranges for analog points.

I exported tags into csv using Controllogix 5000, but I do not see ranges/0&span (Engineering Units) for analog points. What am I missing? Any related input is greatly appreciated.

By Bob Peterson on 31 January, 2018 - 9:23 am
1 out of 1 members thought this post was helpful...

Controllogix tags don't generally have range or engineering unit information built into them unless it is a UDT or an AOI
type tag that has been made to have those features. Standard tags just
don't have them.

By descrambled1 on 31 January, 2018 - 10:27 am
1 out of 1 members thought this post was helpful...

I found out that ranges are stored on the IO modules, which is not a part of tag export.

What about analog tags that come across Modbus TCP datalink? Where are their ranges defined and how can they be exported?

1 out of 1 members thought this post was helpful...

You have to look at the module configuration to see how it is set up.