Monday, May 21, 2018
How to Configure the ROTORK ACTUATOR IQ Range
Need help from experienced guys on how to configure the ROTORK ACTUATOR IQ RANGE to close and open from DCS
By Amar DAMENE on 19 April, 2018 - 2:53 am
Hi all,
Actually I am doing precommissioning for MOV valve using ROTORK Actuator IQ range. Actually, the Actuator is installed on the MOV and all cables are connected to DCS
I tried on site to close and open the vale with selector on LOCAL. it runs good.
BUT
When I select REMOTE on site, on DCS the signal REMOTE is displayed only one second; then I cannot open and close from DCS.
I need your help
These all data about the vale and ROTORK actuator
REPERE 009-MOV-402
FONCTION VANNE MOV SORTIE RAMPE DE COMPTAGE 4
TYPOLOGIE BOISSEAU SPHERIQUE
BRIDE TAILLE 24
TROU TAILLE 24
FAIL ACTION BLOQUEE A LA MEME POSITION (FAIL LAST)
FABRICANT O.M.S. SALERI
MODELE S7100.T.AW.SF.600.EP
TEMPS OUVERTURE/ FERMATURE 3 sec/inch - 3 sec/inch
ACTIONNEUR
TYPE ELECTRIQUE
ALIMENTATION (Alimentation Principale) 400 Vca 50Hz 3Ph
ALIMENTATION (Circuit Auxiliaire) 24 Vdc
FABRICANT ROTORK
MODELE IQ20 B4 96RPM 400/3/50
OVERRIDE ROUE MANUEL
Drawing : RWS100 (100B0000-6)
Wire ACtuator to DCS action
6-7 limit switch Close
8-9 limit switch open
10-11 LOCAL/REMOTE
42-43 FAULT
33-34 CLOSE COMMAND
35 OPEN COMMAND
5 STOP COMMAND
I used a Bluetooth to configure but it is not easy for me
Thanks for your help
You need more information, and you should understand how the DCS logic is set up, and does it match how the Rotork is set up. You need to understand why the remote indication is only on for a second. Look at the input on the DCS (wires 10-11 from the Rotork.) Is it just a pulse from the Rotork? I don't know if that is a setting in the Rotork (pulse for remote). If it is a setting, you may need to change it from pulse to constant. You should monitor the DCS input and outputs (open and close). Make sure you do not have a stop command held in from the DCS. Check to see if it is supposed to be a stop command. Or I have seen a run command that needs to be constant then you have an open or close pulse.
Good luck!
By Amar DAMENE on 21 April, 2018 - 8:18 am
Should I use the 24 VDC from Actuator or 24 VDC from DC?
By borrellimd on 1 May, 2018 - 11:53 am
Usually that depends on whether or not the Rotork has an isolated contact output (sometimes a device will use a triac/digital output that is not isolated.). I'm pretty sure the Rotork uses an actual dry contact from a switch. In that case you would need to power the contact, and the DCS can supply that contact power (usually a jumper or config to make the contact powered by the DCS.).
Good Luck!