Configure OPC using TWIDO via a direct MODBUS connection.
New Replies:
By Schneider Brazil on 26 February, 2010 - 12:35 pm -
What is the OPC Server ? Is it a Schneider OFS ?...
Experiencing odd problems with the ratcheting gear
New Replies:
By BigTom209 on 26 February, 2010 - 10:00 am -
Minister,
Temps maybe somewhat of an issue, but not overheating. We operate in Northern Canada...
By minister on 26 February, 2010 - 3:48 am -
Hi,
We have the DC motor on our ratcheting system (Frame 5).
I read whole the post briefly...
Some character isn't "translating" correctly in the video reference (the one between view...
By BigTom209 on 23 February, 2010 - 12:56 pm -
Another thing I just found out and should mention, originally this was installed with a speedtronic...
Sorry for the late reply, been on the road a few thousand miles this last couple weeks to various...
BigTom209,
How is the troubleshooting going?
Can you tell us what you've found?
Thanks.
...
When did the problem start? It's presumed (because you didn't say so) that it was working fine and...
hart physical layer testing - noise sensitivity test
Advantages of historized process tags in History module over PHD (plant historian database) for panel operators monitoring purpose.
Need for technical manual of Elektronikon MKIV controller from Atlas Copco
New Replies:
By ETURU on 25 February, 2010 - 2:06 am -
Hi,
first of all you have to buy a communication module for profibus, modbus or others at Atlas...
IPC and Load Control doubts for GE steam turbine running on Mark V
New Replies:
By Juan on 24 February, 2010 - 6:31 pm -
Two years ago our ST was a similar state when the IPC was on. We investigate and discovered that...
Can anyone tell me what difference between EEx ia and EEx [ia] and [EEx ia]?
New Replies:
By Allan Jamison on 23 February, 2010 - 4:39 pm -
Bruce
Do you publish or recommend a book on this subject I'm impressed by your knowledge and...
Looking to rent / borrow a calibrator for Honeywell Mag Meter.
New Replies:
By Walt Boyes on 23 February, 2010 - 3:40 pm -
Tom, if it is more than a couple of years old (five or so), it is almost certainly a rebadged...
Mark VI not working with a VCMI board replacement!!
Thickness measurement of a gel film
from the can I fix everything department...
What should we choose Mark VIe Simplex, Dual or TMR configuration?pros and cons for the different configuration Simplex, Dual and TMR
New Replies:
> GE propose simplex, dual and TMR, which is the more suitable configuration for my application....
Speaking as a former GE engineer, for new gas turbine and steam turbine applications, GE will...
Questions regarding removing Reset for PID tuning with the Yokogawa system
What are the precautions and ground resistance to be followed when Yokogawa's CS-3000 interface with a SIEMENS SIMOCODE Starters using profibus-DP.
New Replies:
What are you calling spurious trips? Are you loosing communications with other Simocodes? If so for...
GE MARK V Manuals
New Replies:
By sony on 21 February, 2010 - 9:19 pm -
Hi BB,
would you like to send it to me too. I need it (Speedtronic Mark VI manual, GEH-5979,...
Does anyone have experience/knowledge of measuring saturated steam flowing vertically down using an orifice plate?
New Replies:
By instruguy on 21 February, 2010 - 3:14 pm -
We have used flow nozzle and not orifice plate for steam flow measurement and flow was vertically...
Problems installing Unity Pro on Server 2003R2
New Replies:
By Miguel Lage on 19 February, 2010 - 9:46 am -
We had the same problem, and at last we discovered that in the copy of the software there is an...
Siemens Step7 with PID SIMO (single input, multiple outputs)
Anyone have the pinout from Telemecanique's Altivar 31 RJ45 to RS485?
New Replies:
By andrew aspelund on 18 February, 2010 - 7:29 am -
i wondering if you still have the pin out if i could have it too thank you ...
need help to explain about Exhaust Temperature Feedback and Protection BBL form Mark v
New Replies:
dear CSA,
thank you very much for your help..
regards
pklman...
pklman,
The Mark V operator interface has a "list" of all of the inputs and outputs of...
thank you for your link,
if our unit has 24 exhaust thermocouple,how many T/C signal for each...
Have you looked at this thread:
http://control.com/thread/1260993438
Do you still have...
What kind of processor is the Westinghouse WDPF and what is its intended use?
New Replies:
By NRG on 17 February, 2010 - 10:34 am -
Mr DC,
Please let me know if you are interested in pursuing a WDPF II project. we need to...
want to know about power supply use in ac-450 controller
New Replies:
By Bob on 17 February, 2010 - 6:42 am -
The bulk power supply that drives the SR511 for the AC450 rack is the SA167. Part number is...
The Endress Hauer Tank Level Ultra sonic sensor does not give an stable reading
Creating homegrown PLC hardware
New Replies:
By curt wuollet on 16 February, 2010 - 1:42 pm -
It need to be said that your input is greatly appreciated and any difference of opinion is purely...
Accuracy required for gas custody meter
Pros and Cons Between Message Commands and Producer/Consumer Tags
New Replies:
By James Ingraham on 15 February, 2010 - 3:27 pm -
Neither is "better." It's a question of preference, really.
Pros of Produced /...
exhaust pressure of gt increasing during combined cycle
New Replies:
The exhaust back pressure is higher in combined cycle due to the heat recovery equipment in the...
CBCT connection in power plant
New Replies:
By vijay on 15 February, 2010 - 4:35 am -
dear friend.
it is very hard to detect this kind of problem if power is transmitted through...
Experience with MKVIe for LM-DLE-Engines?
New Replies:
I believe there are many new aero-derivative units being run by Mark VIe turbine control systems.
...
Developing the best tools and practices to develop a new Generic PLC Ladder Editor.
New Replies:
By M Griffin on 11 February, 2010 - 6:51 pm -
In reply to Ken E: The problem with the older bus standards is that the supply of interface chips...
By Ken E on 11 February, 2010 - 8:47 am -
Hi Bill,
Oh yeah, I've seen A LOT of STD bus boards! Just last year I had to have some legacy...
Does grounding the negative side of a power supply make it a grounded conductor.
New Replies:
By Ronald Baggett on 11 February, 2010 - 3:21 pm -
Typically, a grounded conductor refers to AC applications. Grounding the 0V dc output may defeat...
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.