SRV position at valve full close position was found negative 4.2% and LVDT voltage was 0.625V. we did calibration after adjusting LVDT to 0.7 v and auto calibration showed 0.2 %. After one day operation, when the unit was stopped the valve position again shows negative 4.2%. Actual valve...
We have installed MarkVie control system recently. We have printing problem now. Printer stops printing very often. We have to stop and start the project / HMI to resume printing. do anybody face this problem?
Hello,
We have MarkVie system. I have few issues with alarm display and printing.
1- Alarm display is not fully seen in display page. It goes beyond the page and no scrolling facility.
2-Alarms and messages gets truncated in printer. Only partially prints
3- Alarm lock facility not...
we are using honey well flame scanner P/N261A812P012 for MarkVIE. But this scanner is not good for diesel fuel operation. I believe GE recommends to use Geiger-Mueller scanner. Has anybody knows the Geiger-Mueller Part number for MarkVie flame scanner.
Is anybody know where can I get the analog input scale values in MarkV other than Io.asg.list. Also How can I force analog value in MarkV? Please advice.
I would like to edit a ladder logic. the procedure I follow is like this.
Make necessary editing and save the sequence edit file. then table_compile followed by eeprom. Is this correct. Can anyone assist?
After replacing the srv servo valve, we checked the LVDT voltages and found as 0.74 V at 0%. Actual valve position is also -0.1 % in HMI.
In machine operation, srv passes even when it is in negative position (-2.1%) shown by the HMI value.
I tried to put -10% value and got LVDT voltage as...