1761 net dni to cn2dn

J

Thread Starter

jaci fuentes

How i can do a connection (mapping) from Devicenet to a ControlNet using a DNI attach to a micrologix 1500 and a 1788CN2DN ?

I try to map a DNI but the Bridge CN2DN status led is red, RSNetowrx send me a warning about I/O in the DNI..
 
L

Lars-Gosta Johansson

I recognise the problem you mention. In some cases the default I/O size for the CN2DN wich is 124 IN and 123 OUT is to big for ControlNet to handle. Try to decrease the I/O size to some lower value you need.
 