C
Good afternoon guys and gals,
So we are running outputs from our micrologix 1100 to a terminal strip, then out to some relays. I have an 24vdc 8amp power supply
Here's my question, I'm looking at a multi conductor cable going to the junction box 12c 18awg, roughly 300 feet.
From there I want to run 2c 18awg 200 feet to a relay coil.
Will I be able to fire a 24vdc relay coil that distance? What is the standard resistance on a coil, if there is such a thing. I know the coil will pull in even with a decent voltage drop, but I want to understand the load I'm putting on the coil and the plc.