Earlier in the year I posted the following issue=>
About once a month a QA200 fuse clears on the utility riser at our plant. There has been no indication as to why it blows. We have a 2000 KVA 12470 -> 480volt transformer. On the load (480v) side beyond the main CB there is a fixed bank of 400 KVar caps installed. We have had no indication of faults in the load side, and in fact, as soon as the fuse is replaced we can start up and run everything as normal. The Utility is at a loss to explain the problem. My question is, "can the fixed caps be creating problems on the line side of the transformer causing the fuse to heat?"
See the thread http://www.control.com/thread/1026230518#1026237537
The utility’s answer was to replace the transformer and they did so in February.
Since the transformer was replaced we have not had the outage issues that we had in the past. However, two banks of capacitors on the load side of the transformer have ruptured and blown all three phase fuses protecting the caps. The banks are 100 kVar each and the ruptured caps comprise ½ of the total fixed bank. The capacitors did not rupture at the same time, in fact the last bank to rupture appears to have happened within the last week. What might cause the caps to rupture and blow the fuses?
About once a month a QA200 fuse clears on the utility riser at our plant. There has been no indication as to why it blows. We have a 2000 KVA 12470 -> 480volt transformer. On the load (480v) side beyond the main CB there is a fixed bank of 400 KVar caps installed. We have had no indication of faults in the load side, and in fact, as soon as the fuse is replaced we can start up and run everything as normal. The Utility is at a loss to explain the problem. My question is, "can the fixed caps be creating problems on the line side of the transformer causing the fuse to heat?"
See the thread http://www.control.com/thread/1026230518#1026237537
The utility’s answer was to replace the transformer and they did so in February.
Since the transformer was replaced we have not had the outage issues that we had in the past. However, two banks of capacitors on the load side of the transformer have ruptured and blown all three phase fuses protecting the caps. The banks are 100 kVar each and the ruptured caps comprise ½ of the total fixed bank. The capacitors did not rupture at the same time, in fact the last bank to rupture appears to have happened within the last week. What might cause the caps to rupture and blow the fuses?