AB PLC 5/40C vs SLC45/04

P

Thread Starter

Pedro_Miguel_Carri

Dear srs:


I have a project and the system integrator suggest to use PLC 5/40 with ControlNet i prefer to use the SLC5/04 with a controlnet communication card instead , because we don not work with many analog signals and no more than 120 discretes signals. I want to know if some of you have noted certain differences in peformance and reliability between AB SLC and PLC processors


Regards,

Pedro M. Carri
 
Just my $.02 worth but I wouldn't use either PLC-5 or SLC. I would suggest looking at the FlexLogix processor with Flex I/O. Cost would be much less than PLC-5/40C and probably less than SLC-5/04, 5/05 also.

For ControlNet add the ControlNet daughtercard and for Ethernet add the Ethernet/IP daughtercard and away you go.

The Flex system will have a much longer usable life span than the PLC-5 and SLC machines. Also would provide the opportunity to "get your feet wet" with the new breed of A-B controllers.

Bradley G. Hite
Intertech Inc.
mailto:[email protected]
http://www.myplc.comTeaching Practical Skills for a Technological World
 
T

Trevor Ousey

My preference would be a PLC5 over an SLC5, but if you dont need the power and stuff it would be hard to justify. Other benefits are the DH+/RIO are definitely easier/better on PLC5's. And then if I was going to do a new PLC I would go Controllogix.
 
J

Jeremy Pollard

Large cost differnece as well as an enhanced instruction set for the 5/40. The integrator may find the code easier to write with a 5/40 than a 5/04. If not then stick to your guns. Less money out of your pocket

Cheers from:

Jeremy Pollard, CET
[email protected]
On The Web - http://www.tsuonline.com
PLCopen North America - [email protected] www.PLCopen.org
the Training Factory, Inc.
Programmable Controller Support Systems
The Software User Newsletter ONLINE
The Crazy Canuckian!
8 Vine Crescent, Barrie, Ontario L4N 2B3
705.739.7155 Fax 705.739.7157
 
Top