I am unable to let you have our only copy of the SLC 100 manual but if you describe you requirements in detail I will help. Either with info from the manual or some suggestions for the code. if you wish contact me direct [email protected]
Hi Ken,
Thanx for reply and offer.
It is a simple on /off timer combined with a counter that I require.
When I "close" a contact (1 or 101) I wish to initiate a sequence where output 11 will be turned on for a determined time (~ 10 seconds) and then turned off for a determined time (likely the same value). This is to be considered one cycle and I would like to count (up or down) 500 cycles and then stop the process. A very handy feature would be a "pause" where if I closed the next contact (2 or 102) the timing and counter would pause until I opened the contact at which point it would resume. I was hoping the "count" could be displayed on my handheld programmer (1745-PT1)but it is not strictly necessary.
Ditch the old SLC, get a LOGO! or other programmable relay program from the front with no software Smaller, more efficient etc. etc.
cost you about 75 Euros
rung 1 latches the state of input 1 (note the process will recycle after 500 counts unless I/P 1 is turned off or you add a one shot
rung 2 starts the first timer (set to 10 secs) unless I/P 2 is turned On
rung 3 runs the second timer
rung 4 counts the required cycles
rungs 5 and 6 reset the timers each cycle
rung 7 stops the operation at the end of 500 cycles
rung 8 resets the cycle count
rung 9 turns ON O/P 11 each cycle
I agree there are many newer (better?) devices available but assume you need to work with what you have.