ABB ACS 550 and RPBA-01

H

Thread Starter

Hidde Hekker

I'm using an ABB ACS 550 with an profibus communication card RPBA-01. This is communicating with an S7-400 on the basis of an PPO-4 protocol. Now I want the value written by the S7-400 in PZD3 will be placed in an certain menu (menu 112). How do I do this, i look in the documentation and that doesn't tell me alote.
 
S

Stefaan Van Eenoo

With parameter 51-5 you define the place where PZD-3 will be written to. See page 24-25 of the manual of the RPBA-01.

BTW: with group & parameter do you mean with 112 ? Group 1 - Parameter 12 or Group 11 - Parameter 2 or Group 112 - Parameter x

HTH,
Stef
 
J

Joe Blasczyk - ABB US

The Ref2 value must be written by selecting PZD3 (51.05) to a value of 3. The Actual value signal at Menu 112 is a read only parameter. All other groups 10 thru 98 are R/W parameters. If you any further questions please feel free to contact me at 1-262-785-3533.
 