We are operating 2 frame 6 B DLN-1 machine (Only Gas fuel) in middle east for meeting out power requirements in process plant. The ambient temp remains above 40 Deg C. The accessory compartment temperature as per GE is 60 Deg C. The ambient temperature of this motor shown as per manual as 40 Deg C.
Thermal imaging was done and temperature is around 60° C during day hours and on the running equipment the temperature reach 90 - 100° C
which cause overheating of cables, windings, cooling fan of motors. Acc cooling fan motor 88 BA 1 & 2 has burnt 3 times in a span of 2 years. The fan of motor is non metallic and gets melted. The motor is EX Motor and its protection EEx e II T3.
I like to know is it normal to have acc compartment temp 60 Deg C and on the running equipment the temperature reach 90 - 100° C or any flue gas ingress.
88BA1 &2 cooling fan of motor is it non metallic generally? (Pl note the fan 88BA 1 & 2 is metallic. The cooling fan of motor is non-metallic.)
Is there alternative motor meeting the same specification?
Is it advisable to shift the motor outside the compartment out side the acc compartment keeping fan inside and having a sealing to protect the CO2 flooding system effectiveness?
Thermal imaging was done and temperature is around 60° C during day hours and on the running equipment the temperature reach 90 - 100° C
which cause overheating of cables, windings, cooling fan of motors. Acc cooling fan motor 88 BA 1 & 2 has burnt 3 times in a span of 2 years. The fan of motor is non metallic and gets melted. The motor is EX Motor and its protection EEx e II T3.
I like to know is it normal to have acc compartment temp 60 Deg C and on the running equipment the temperature reach 90 - 100° C or any flue gas ingress.
88BA1 &2 cooling fan of motor is it non metallic generally? (Pl note the fan 88BA 1 & 2 is metallic. The cooling fan of motor is non-metallic.)
Is there alternative motor meeting the same specification?
Is it advisable to shift the motor outside the compartment out side the acc compartment keeping fan inside and having a sealing to protect the CO2 flooding system effectiveness?