Allen Bradley SLC 150 conversion to SLC 501

L

Thread Starter

Larry Davis

I have written a translation/conversion of a slc 150 to RS Logix program and have only one question, How do I treat the MCR and zcl commands in the new 501 program?? thanks Larry
 
B

bob peterson

I think the MCR works the same way in the slc500 as they do in the slc150.

ZCL is more like a jmp IIRC.

--
Bob
 
J

Jeremy Pollard

MCR .. If resulting instruction set doesn't have an MCR inst, then use a tmp bit and put and XIC in each rung of the following rungs

ZCL - Zone Control - use a JMP..