We are using an Allen Bradley SLC-5/05 in Chassis 0 with a 1746-SN Scanner to communicate with three 1794-ASB/D Remote I/O Adapters (Racks 1-3) along with their associated Flex I/O Modules. Periodically the last rack (Rack 3) faults for no apparant reason and indicates that the PLC is in Program/Test mode even though it is still in Run Mode (Local Fault LED = Off; Adapter Fault LED = Off and Adapter Active LED = Blinking).
RIO Communications can operate flawlessly for long periods of time between faults or sometimes can fault several times within hours. It is totally unpredictable (intermittant). The baud rate is set at 57.6k and a 150 ohm terminating resister is installed at both the scanner end and the last physical device end (I/O Adapter for Rack 3). Initially, since the last chassis was always the one to fault, we suspected that the problem might be the setting of dip switch S2-6 which defines which Chassis is the last one. Allen Bradley said that this dip switch setting is irrelevant with all 1794-ASB RIO Adapters above Series B. Since all of our adapters are Series D we eliminated this as the potential cause. Any/all suggestions would be appreciated. Thank you!
RIO Communications can operate flawlessly for long periods of time between faults or sometimes can fault several times within hours. It is totally unpredictable (intermittant). The baud rate is set at 57.6k and a 150 ohm terminating resister is installed at both the scanner end and the last physical device end (I/O Adapter for Rack 3). Initially, since the last chassis was always the one to fault, we suspected that the problem might be the setting of dip switch S2-6 which defines which Chassis is the last one. Allen Bradley said that this dip switch setting is irrelevant with all 1794-ASB RIO Adapters above Series B. Since all of our adapters are Series D we eliminated this as the potential cause. Any/all suggestions would be appreciated. Thank you!