Breaker first pole to clear factor

K

Thread Starter

Krishna

How is the value of C.B first pole to clear factor derived 1.3 for solidly earthed system?
 
P

Phil Corso,PE

Actually, it comes from ANSI C37.04! But please note that it is the asymmetrical (rms)-to-symetrical (rms) current. It is not, repeat, not the first-cycle peak.
 
A transient recovery voltage (or TRV) for high-voltage circuit breakers is the voltage that appears across the terminals after current interruption. It is a critical parameter for fault interruption by a high-voltage circuit breaker, its characteristics (amplitude, rate of rise) can lead either to a successful current interruption or to a failure (called reignition or restrike).
The TRV is dependent on the characteristics of the system connected on both terminals of the circuit-breaker, and on the type of fault that this circuit breaker has to interrupt (single, double or three-phase faults, grounded or ungrounded fault).

Characteristics of the system include:
- Type of neutral (effectively grounded, ungrounded, solidly grounded)
- Type of load (capacitive, inductive, resistive)
- Type of connection: cable connected, line connected

The most severe TRV is applied on the first pole of a circuit breaker that interrupts current (called the first-pole-to-clear in a three-phase system).
 
N

nilesh pagare

First pole to clear factor is the ratio of distance between faulty phase and healthy phase to the faulty phase. The value should not come more than 1.5.
 
K
> How is the value of C.B first pole to clear factor derived 1.3 for solidly earthed system?

Formula for the first-pole-to-clear factor=Kpp=
=3Xo/(2X1+X0)
where X0 is the zero sequence, and X1 the positive sequence reactance of the system
 