Citect scada support for allen bradley micrologix 1000

J

Thread Starter

Joshin Joy

i need to know whether Allen Bradley micrologix 1000 is supported by citect scada 6

please help how to configure it
 
W

Wassim Daoud

Are you using OPC for this? With OPC, your Citect scada will be able to support the Allen Bradley.

All you need to is connect an OPC Server for Allen Bradley to the OPC Client in the Citect Scada. Here is link to the OPC Server for Allen Bradley:

http://is.gd/fn92A

Wassim Daoud
Global Solutions Architect
 
T

Trevor Ousey

Hi, the simplest way is to set it up as a serial DF1 driver the same as with an SLC. No need to get any other third party IO servers as this is supported in Citect.
 
J
> the simplest way is to set it up as a serial DF1 driver the same as
> with an SLC.

i tried it. but micrologix 1000 supports DF1 full duplex communication the citect SLC is DF1 Half duplex and is not supported
 
J
> Are you using OPC for this? With OPC, your Citect scada will be able to support the Allen Bradley. <

Sir,
i downloaded the matrikon opc for allen bradley.

can you please tell more how to configure it with citect scada. i did many methods and was not successful.
 
W

Wiwi Hartono

Hi,

There are few options listed below for Citect to communicate with AB Micrologix and vice versa.

Citect driver: ABMLXEIP (EIP)
AB Hardware Requirements = 1761 NET-ENI Module

Citect driver: ABRSLINX
AB Software Requirements = ABRSLinx

Citect driver: OPC
AB Software Requirements = RSlinx OPC Server

Hope this help.
 
Top