Citect to EGX200 to Sepam 40

T

Thread Starter

twtysvn

When I'm connecting some Sepam series 40 to an EGX200 gateway and the EGX to a CitectSCADA application, and when I set up the variable tags in Citect, what should I enter in the Address field? For example, if I need to get data from a word in the Sepam, what should I enter in the Address field in Citect?

Sorry for my bad english! Thank you!
 
A

Albert Olive

- Firstly you need to select inside the Express Communication Wizard Menu the Disc IO Device (not External or Memory IO Device). With this selection you will connect with a PLC simulator.

- The next screen shows the list of Citect drivers . Select Tsx-Quantum (Ethernet TCP/IP) driver (Modnet driver)

- Inside the next Wizard screen select the IP address of EGX200 and 502 port (Modbus port)

- When the Wizard setup is finish, you will need define de IODevice. Inside Citect Project editor select Communication - IODevice. Inside the field Address, you should put the Modbus address of the SEPAM40.
 
Top