We are operating GE Frame 9E open cycle Gas Turbine for a peak load. The GT now is experiencing temperature spread problem caused by thermocouple at location P,Q,R,S location (lower temperature than the rest) that caused high temp diff. This triggered the alarm (about 140 deg C diff between lowest and highest temp of thermocouple raedings). The GT cannot go to base load as it may trip, so it is now limited to about 85MW.Suspecting it could be the burners problem we replaced about 5 burners corresponding to the thermocoule position (referring to the GE swirl chart). The problem solved for about 2 weeks but since has recurred. Now we are suspecting the GCV as it shows opening at 55% at about 85 MW loading (normally it should be 50%). There is also observation of a brownish colored smoke coming out during the GT loading at 85 MW, which could explain of incomplete combustion. Hope you can give some pointers. Thank You.