Comms between 135U Siemens and Controllogix CPU

R

Thread Starter

Roberto

Hello nerds,

I need to communicate from a 135U 928B CPU with a Contrologix CPU. Communication does not have to be fast, so tought of using the available slot in wich i can stick a serial adaptor. And then use the serial port on the controllogix CPU.

But how do I make this work and is this possible.

Greetings
Roberto
 
J

Jerry Miille

You can look at our Omnii-Comm product for this application http://www.miille.com/din266-p00.pdf This could provide a ready to go solution for your application. It supports over 60 protocols and can connect directly to the ControlLogix DF-1 serial port. No PLC programming is required.

Jerry Miille
 
J

John Barnet Engineering

The best way is to use a Profibus card in the Control Logix (Prosoft makes a good one) and put a Profibus DP Slave card in the S5 PLC. Then you got a simple data transfer from one to the other. Be careful if you are using floating point numbers as the Control Logix treats them differently than the S5 and you might have to swap the bytes.
 