A have a PLC Siemens S7-200 (CPU 226 COD. 6ES7 216-2BD23-OXBO) and a Simatic Panel TP177. I desire to collect data on a workstation. Is it possible to communicate directly without any additional interface? With Modbus perhaps?
Hi,
Sorry, but the Siemens S7-200 DOES use MODBUS, and there is a perfectly good MODBUS master available in the libraries, I have several projects running Remote IO via MODBUS from S7-200s.
The latest MODBUS Master library is v1.2 and you may use either port, MODBUS Slave is available as v1.0 only on Port 0
The CPU 226 has two RS 485 ports as standard and Siemens offers a Modbus Protocol Library you can install to allow one of the ports to communicate as a Modbus Master or Slave. All you will need is a RS 485 port on your PC or an RS 485 to RS 232 converter.
Thank you,
David Adams
Application Engineer
CONTROL PRODUCTS [email protected]
334-567-2017 office
334-567-8614 fax
334-303-9499 cell
pvbrowser should check the facts before he replies. Siemens has Modbus drivers for both the S7-200 and the S7-300. i think in this day and time any good PLC manufacturer that has a serial card can talk Modbus.
But according to the commentary by David Adams, I feel good option, but how do I do with communication to Simatic Panel?, taking into account that I leave a free port for maintenance and scheduling.
The above modbus solution from Siemens is for Modbus/TCP only. If somebody knows a modbus solution from Siemens which works with an RS232/RS485 converter please let me know.