Communication between Sepam and Quantum PLC

Y

Thread Starter

Yve ZH

I need to read data from Sepam with the RS-232 port of Quantum CPU, is any one to tell me how to do it?
 
I've connected 3 separate networks each with 1 Quantum 434 and 8 Sepam 2000 on Modbus RTU. For Quantum you should use XMIT. It came as Loadable and if you don't have it I can provide it to you. This XMIT will only attache itself as Master on COMM1 in Quantum. Sepam 2000 use an RS-485 port to implement the network. For this reason you have to use an RS232 to RS485 converter. The speed of the network can be up to 19.200 kB

Good luck.
 