compatiblity of 3-wire gas detector to 2-wire term panel of triconex

V

Thread Starter

vijay

I would like to know whether a 3-wire gas detector can be compatible with 2-wire External Termination panel connected to a 2-wire Anaglog Input Module in PLC
 
R
Yes it can be compatible if both the module and detector are zero based, most are. The transmitter should be expecting the PLC to be connected between it's output and -24 VDC.

Post your transmitter and PLC IO model nos and someone will check it.

Regards,
Roy
 