Conductor Sizing

C

Thread Starter

Carl Jorgensen

I need information on sizing conductors. I need to carry <=150VDC @ a max of 1ma. It can be at frequencies up to 20Khz. I need to find the
smallest wire possible, preferably something that can be mass terminated due to the number of connections needed.
Thank you
 
M

Michael Griffin

>I need information on sizing conductors. I need to carry <=150VDC @ a
>max of 1ma. It can be at frequencies up to 20Khz. I need to find the
>smallest wire possible, preferably something that can be mass
>terminated due to the number of connections needed.
<clip>

The amount of current you mention (1 ma), is too small to be a major consideration for any normal conductor size available. Even a normal ribbon cable can carry many times this amount. You need instead, to worry about the voltage rating and other factors such as avoiding problems with cross-talk between the conductors in the frequency range you listed.
The best solution to this problem will depend upon various installation factors which are particular to your application.


**********************
Michael Griffin
London, Ont. Canada
**********************
 