In most control panels, no neutral wire is used, i.e, a line voltage (phase to phase) have been given to a transformer wich gives a phase to ground voltage (normally 220 or 110 volts).
I've heared two reasons for this:
1. To reduce the load of neutral earth (loadability)
2. To isolate the feeding power from the main power network
I suppose that the first reason is fairly right but the second is not completey right, because although the energy is transfered via a magnetic media, every short circuit in one side of the transformer will be transfered to the other side.
1. Is there any other reason for that?
2. What is your opinion about using the above mentioned method instead of simply using a phase to neutral connection to supply the PLCs and other single phase consumers?
3. Normally, one of the two wires of the transformer secondary is connected to earth. Do it must be connected to the Protective Earth (PE), or Neutral or Null Earth (N) in separated systems (TNS or 5 wire systems)?
I've heared two reasons for this:
1. To reduce the load of neutral earth (loadability)
2. To isolate the feeding power from the main power network
I suppose that the first reason is fairly right but the second is not completey right, because although the energy is transfered via a magnetic media, every short circuit in one side of the transformer will be transfered to the other side.
1. Is there any other reason for that?
2. What is your opinion about using the above mentioned method instead of simply using a phase to neutral connection to supply the PLCs and other single phase consumers?
3. Normally, one of the two wires of the transformer secondary is connected to earth. Do it must be connected to the Protective Earth (PE), or Neutral or Null Earth (N) in separated systems (TNS or 5 wire systems)?