controlling drum level

Hi,

I had heard about 3 element but never 5 & 7. May be if you are looking for 3 element boiler drum level control then have a look at Yokogawa US1000 controller.

Hope this helps.

Regards
 
It is never 5 or 7 element control. It is always 3-element control. Some people add some more parameters like density compensation (substract the rate of change of Stm Pr) & call elements of control. So what you know of 3-element control is correct.

Dev
Siemens
 
A

abhishek Srivastava

Dear Sneha Goel,

I want to know the control logic of three element drum control with steam flow & drum density calulation. Please send the logic with detail.

Abhishek srivastav
spray engineering device limited
09882113455
 
V

vithal s. pawitwar

These 7 parameters are:
1] drum level
2] feed water flow
3] steam flow
4] steam temperature
5] feed water temperature
6] steam pressure
7] feed water pressure
 
V

vithal pawitwar

Hi...

There is one chart for that where we use it. This chart is between pressure and density. We use this in program as y=F(x).

Initially we use single element control, then we go for 3 element control.

vithal pawitwar
vedanta aluminum ltd.
 
S

SOMNATH KELKAR

Hi,

Five/Seven element Frum level control means Three nos {(DRUM) LT, PT} {(STEAM) FT, PT, TT} and FEED WATER (FT). When all these measurements are taken then it is seven Element Drum Level Control.

Regards
Somnath Kelkar (INDIA-PUNE)
somkel [at] gmail.com
 