Greetings!
I am currently having trouble in controlling the danfoss FC302 VLT in MODBUS RTU protocol using FP-X Panasonic C30R plc in RS-485 comm. can you pls sir give me a link where to find the modbus fc302 manual? Below is the PLC program and FC302 danfoss configuration i've made.
Note: For the basic application sir, pls give me sample program/modbus rtu command in running forward motor with respect to the modbus manual if possible sir kindly specify to what register in the manual.
Danfoss Settings:
0-** Operation/Display
0-4 LCP Keypad
0-40 [Hand On] Key on LCP – Disabled // to remotely run the inverter using PLC command
0-41 [Off] Key on LCP - Enabled
0-42 [Auto on] Key on LCP – Enabled
0-43 [Reset] ] Key on LCP – Enabled
3-** Reference/Ramps
3-13 Reference site – Local // to manually adjust the Frequency of the inverter via keypad
5-** Digital In/Out
5-10 Terminal 18 – No operation
5-11 Terminal 19 – No operation
5-12 Terminal 27 – No operation
8-** Comm and Options
8-0* General Settins
8-01 Control Site – [0] Dig. And Word
8-02 Control Word and Source – [1] FC RS485 // for RS485 Comm
8-1* Control settings
8-10 Control word Profile – [0] FC Profile
8-3* FC Port Settings
8-30 Protocol – [2] Modbus RTU
8-31 Address – 03 //inverter Address
8-32 Baud rate – [7] 115200//same baud rate in the plc comm. Set-up
8-33 Parity/Stop bits – [0] even parity,1 stop bit //same also in the PLC comm. Set up
PLC Program
COMPORT SELECTION
Note:
Comport 1 comm mode – MEWTOCOL-COM Master or slave unit //for rs232 comm port PC to PLC interface
Baud rate = 115200 // same in the FC 302 inverter
Data length = 8 bita with odd parity and 1 stop bit
Comport 2 comm mode – Modbus RTU Master/Slave
Comport 2 selection – Comm3 cassette[RS485] PLC interface
Baud rate = 115200 // same in the FC 302 inverter
Data length = 8 bita with odd parity and 1 stop bit
TOOL Port SELECTION
\
Note: Tool port Comm = MEWTOCOL-COM Master or slave unit //for rs232 comm port PC to PLC interface
PLC Program
Y0 – start enable of the modbus command
Port – com 2 // rs485 interface
Function code – sys_modbus_15_force coils
Start Register – 0002H
Number of registers – 1
Master Data – DT100[16#047c]
Sys_com1_trxdone – check com 1 transmission
Sys_com2_trxdone – check com 2 transmission
Actual Set-up
Since i cannot post the PLC program with the PLC settings and configuration i can provide it by giving you my email add: [email protected]
Thank you soomuch..God bless!!!
I am currently having trouble in controlling the danfoss FC302 VLT in MODBUS RTU protocol using FP-X Panasonic C30R plc in RS-485 comm. can you pls sir give me a link where to find the modbus fc302 manual? Below is the PLC program and FC302 danfoss configuration i've made.
Note: For the basic application sir, pls give me sample program/modbus rtu command in running forward motor with respect to the modbus manual if possible sir kindly specify to what register in the manual.
Danfoss Settings:
0-** Operation/Display
0-4 LCP Keypad
0-40 [Hand On] Key on LCP – Disabled // to remotely run the inverter using PLC command
0-41 [Off] Key on LCP - Enabled
0-42 [Auto on] Key on LCP – Enabled
0-43 [Reset] ] Key on LCP – Enabled
3-** Reference/Ramps
3-13 Reference site – Local // to manually adjust the Frequency of the inverter via keypad
5-** Digital In/Out
5-10 Terminal 18 – No operation
5-11 Terminal 19 – No operation
5-12 Terminal 27 – No operation
8-** Comm and Options
8-0* General Settins
8-01 Control Site – [0] Dig. And Word
8-02 Control Word and Source – [1] FC RS485 // for RS485 Comm
8-1* Control settings
8-10 Control word Profile – [0] FC Profile
8-3* FC Port Settings
8-30 Protocol – [2] Modbus RTU
8-31 Address – 03 //inverter Address
8-32 Baud rate – [7] 115200//same baud rate in the plc comm. Set-up
8-33 Parity/Stop bits – [0] even parity,1 stop bit //same also in the PLC comm. Set up
PLC Program
COMPORT SELECTION
Note:
Comport 1 comm mode – MEWTOCOL-COM Master or slave unit //for rs232 comm port PC to PLC interface
Baud rate = 115200 // same in the FC 302 inverter
Data length = 8 bita with odd parity and 1 stop bit
Comport 2 comm mode – Modbus RTU Master/Slave
Comport 2 selection – Comm3 cassette[RS485] PLC interface
Baud rate = 115200 // same in the FC 302 inverter
Data length = 8 bita with odd parity and 1 stop bit
TOOL Port SELECTION
\
Note: Tool port Comm = MEWTOCOL-COM Master or slave unit //for rs232 comm port PC to PLC interface
PLC Program
Y0 – start enable of the modbus command
Port – com 2 // rs485 interface
Function code – sys_modbus_15_force coils
Start Register – 0002H
Number of registers – 1
Master Data – DT100[16#047c]
Sys_com1_trxdone – check com 1 transmission
Sys_com2_trxdone – check com 2 transmission
Actual Set-up
Since i cannot post the PLC program with the PLC settings and configuration i can provide it by giving you my email add: [email protected]
Thank you soomuch..God bless!!!