OK, but why the normal water level would not be 15 inches with 0 to 30 inches of the total level?Generally, It is a good practice to have the transmitter output match what the operator would see in the gauge glass of the drum. i.e. Normal water level is zero with +/- 15 inches of water level.
Low water level can damage boiler tubes and high water level can cause carryover damage to the equipment driven by steam. The boiler designers deemed normal to be zero and also gave parameters for low and high water level conditions based on boiler design. The normal water level reference is on all boiler designs to give a common reference rather than confusing and differing levels for each boiler. It is easy to remember that zero is normal water rather than a marine D type B&W boiler is 15 and a large power plant Foster Wheeler boiler is 17. By the way, 15 and 17 are made up values. Accepting that normal water level is zero is much easier.OK, but why the normal water level would not be 15 inches with 0 to 30 inches of the total level?
Thanks for your help
Thread starter | Similar threads | Forum | Replies | Date |
B | Drum level and combustion control | Instrumentation & Measurement | 1 | |
K | Drum Level Span | Power Generation | 2 | |
S | Level Gauge on Steam Drum | General Automation Chat | 4 | |
C | Drum Level Fluctuation Due to Rain | Power Generation | 5 | |
E | Boiler Drum Level Control Using Drum Level as a Ramp Function of Operating Power | Process Control | 1 |